Has anyone run across this? Apparently, the compressor breaks down and sends metal shavings throughout the system. Once the accumulator gets clogged, the a/c stops puting out cold air. After 2 hours of troubleshooting, the mechanic finally found the problem. One way of finding it is the high side and low side have the same pressure, indicating a blockage. The thermisters<sp>, orifice filter, and high side pressure switch all had metal shavings on them.
Repair is quite costly, as the compressor and any contaminated components must be replaced. The system has to be flushed, usually several times. And even that doesn't guarantee it to be totally free of shavings.
According to this site, it usually results from either low charge level, or not enough oil in the freon to lubricate the compressor.
http://www.ackits.com/index.cfm?fuseaction=black death
Repair is quite costly, as the compressor and any contaminated components must be replaced. The system has to be flushed, usually several times. And even that doesn't guarantee it to be totally free of shavings.
According to this site, it usually results from either low charge level, or not enough oil in the freon to lubricate the compressor.